Mech
REGISTERED
2015 IBC
Unlimited Area building, Non-separated B, F-2, S-2 use groups with sprinklers.
Maximum travel distance is 400 ft for F-2 and S-2, but only 300 ft for B.
If I want to have people from the F-2 and S-2 areas egress through the B section, what is the maximum travel distance allowed for F-2 and S-2? Would I perform a unity calculation by verifying the ratio of the distance traveled in the F-2 and S-2 area divided by 400 ft (maximum for F-2 and S-2) plus the distance traveled in the B area divided by 300 (max for B) equals less than or equal to 1?
The portion of travel in the B occupancy is through one of two corridors that are each less than 40 ft long and are straight. The corridors have doors opening to offices, toilet rooms, cafeteria, and/or a closet.
Unlimited Area building, Non-separated B, F-2, S-2 use groups with sprinklers.
Maximum travel distance is 400 ft for F-2 and S-2, but only 300 ft for B.
If I want to have people from the F-2 and S-2 areas egress through the B section, what is the maximum travel distance allowed for F-2 and S-2? Would I perform a unity calculation by verifying the ratio of the distance traveled in the F-2 and S-2 area divided by 400 ft (maximum for F-2 and S-2) plus the distance traveled in the B area divided by 300 (max for B) equals less than or equal to 1?