Egress through Intervening Spaces w/ different Max Travel Distances

Mech

REGISTERED
Joined
Oct 30, 2009
Messages
1,054
Location
Eastern PA
2015 IBC

Unlimited Area building, Non-separated B, F-2, S-2 use groups with sprinklers.

Maximum travel distance is 400 ft for F-2 and S-2, but only 300 ft for B.

If I want to have people from the F-2 and S-2 areas egress through the B section, what is the maximum travel distance allowed for F-2 and S-2? Would I perform a unity calculation by verifying the ratio of the distance traveled in the F-2 and S-2 area divided by 400 ft (maximum for F-2 and S-2) plus the distance traveled in the B area divided by 300 (max for B) equals less than or equal to 1?

The portion of travel in the B occupancy is through one of two corridors that are each less than 40 ft long and are straight. The corridors have doors opening to offices, toilet rooms, cafeteria, and/or a closet.
 
I am thinking max is what occupancy you start in

And does not change


Maximum travel distance is 400 ft for F-2 and S-2, but only 300 ft for B.


Interesting question. Will see what others say.


What are the total building dimensions ??

And occupant load?
 
As cda states, it is where you start. If you are in a Group F-2 and you egress through a Group B, you have 400 feet of travel distance permitted. If you are in a Group B and you egress through a Group F-2, you have 300 feet of travel distance permitted.
 
$ ~ $ ~ $

Mech,

FWIW, ...I also agree with
**cda** & **RLGA**.
The actual 400 ft. distance is a non-negotiable
length.......That is the absolute max. distance of travel
permitted, regardless of which Occ. Groups are
egressed through.


$ ~ $ ~ $
 
Its where you start....You don't get more even if you enter a space with more, and certainly not with less....Corridor would not help with TD, Rated EXIT would...
 
Thank you for the replies. I ran out of time last night when writing my post. I wanted to get out of the city before it got too late.

cda - the building is 400,000 sq ft. It is about 785'x510'

I would never increase the max allowable beyond what is written in the code . . . and I would not try to travel 400 ft from F-2 and then an additional 300 ft from B.
 
Thank you for the replies. I ran out of time last night when writing my post. I wanted to get out of the city before it got too late.

cda - the building is 400,000 sq ft. It is about 785'x510'

I would never increase the max allowable beyond what is written in the code . . . and I would not try to travel 400 ft from F-2 and then an additional 300 ft from B.


Add more exit doors in the F-2?
 
More doors or revise the equipment layout would work. The building has been erected under a shell permit. We are preparing an egress plan now that the F-2 / S-2 is being fitted out by the owner.
 