I have a bank we are designing. There is the main bank area. Then a arched opening to a "back of house" area where the toilet rooms, mechanical and break room are located. Only one means of egress is required for the occupant load and travel distance. The exit door in the break room is just employee convienence.
The owner wants to place a passage door separating the bank from the toilet rooms. This would not be locked. However i feel this triggers the "egress through an intervening space" since to exit the toilet room, you then have to pass thru another door to see an exit.
But Im questioning if it would trigger this because these spaces are "accessory" to the bank.
"Egress from a room or space shall not pass through adjoining or intervening rooms or areas, except where such adjoining rooms or areas and the area served are accessory to one or the other, are not a Group H occupancy and provide a discernible path of egress travel to an exit."
What are people opinion on this?

I have a bank we are designing. There is the main bank area. Then a arched opening to a "back of house" area where the toilet rooms, mechanical and break room are located. Only one means of egress is required for the occupant load and travel distance. The exit door in the break room is just employee convienence.
The owner wants to place a passage door separating the bank from the toilet rooms. This would not be locked. However i feel this triggers the "egress through an intervening space" since to exit the toilet room, you then have to pass thru another door to see an exit.
But Im questioning if it would trigger this because these spaces are "accessory" to the bank.
"Egress from a room or space shall not pass through adjoining or intervening rooms or areas, except where such adjoining rooms or areas and the area served are accessory to one or the other, are not a Group H occupancy and provide a discernible path of egress travel to an exit."
What are people opinion on this?