Electric Water Heater
Would you write up this crawlspace install?
I would.
What code in the IRC covers this?
Re: Electric Water Heater
Jeff is that glare from your camera or the required lighting outlet per 210.70(A)(3)?
It did have the required lighting but I never turn the lights on in the crawlspaces as my flashlight works better and I am not "blinded by the light"
Manfred Mann's Earth Band
In the IRC? Table 3702.1 under NM column. Our state adopts the NEC for residential and commercial, so 334.30(2008) as stated above, would apply.
P2803.6.1 Requirements for discharge pipe. The discharge
piping serving a pressure-relief valve, temperature- relief
valve or combination valve shall:
7. Discharge to a termination point that is readily observable
by the building occupants.
mueller said:
P2803.6.1 Requirements for discharge pipe. The dischargepiping serving a pressure-relief valve, temperature- relief
Good point but this is an Electrical topic :)
Prediction,
This is going to be a looong thread.
Uncle Bob
PORTEOUS said:
Yes, 3702.1, and maybe 3509.6, although I cannot tell if there is pex above the copper
Educate me....What does Pex above the copper have to do with anything at this point? Were you thinking the short sections of copper need to be bonded per 250.104 ? Just asking.
Jar,
How about posting the water heater on "Residential Plumbing"; so we can take this baby to the next level; without compromising the Electrical discussion?
This can be a great plumbing topic,
Uncle Bob
Uncle Bob said:
Jar,How about posting the water heater on "Residential Plumbing"; so we can take this baby to the next level; without compromising the Electrical discussion?
Uncle Bob
Done
Greg, I was thinking the short sections would not need bonded as the are interupted and not continious by the pex. Is this interpretation correct? Thanks, Bill
Short sections of metal water piping do not constitute a "piping system" and therefore are not required to be bonded in accordance with 250.104(A).
Chris
Chris
Porteous and Chris yes that was my point. I mis understood you and read too much between your lines. I thought maybe you were thinking that the copper stub ups were requiring bonding.