Berkshire Al
REGISTERED
I own a cabin, constructed in the 1930's on a remote property in Massachusetts, about 8,000 feet and up rugged trails from the nearest street. The current (ninth edition) of the MA State Building Code is based upon the 2015 IRC, which includes a modified version of Appendix J pertaining to existing buildings and structures. The cabin is in poor condition, and I'm evaluating the 4 options under Appendix J - 1) repair, 2) renovation, 3) alteration or 4) reconstruction.
Critical to my evaluation is to understand what is required in association with each of these options. Unlike the repair and renovation options, both alteration and reconstruction require (amongst other things) that electrical services meet certain minimums. See sections AJ501.5.1 and AJ501.5.2 below. The cabin presently does not have any electrical service, and I'd say it would be prohibitively expensive and/or impractical to connect to the street nearly 2 miles away. I do not intend or wish to install an electrical service, as this is a primitive cabin. If I am going to perform an alteration or a reconstruction, do I need to install electrical service? AJ501.5.1 refers to "Newly installed electrical equipment...shall comply...". If there is no electrical equipment being serviced, is it fair to conclude that the provisions related to electrical equipment and wiring (including service to the dwelling unit) do not apply? As an alternative option, would it be possible to comply with these provisions through the installation of a generator?
Thanks in advance for any advice or suggestions,
Al
AJ501.5.1 Materials and methods.
Newly installed electrical equipment and wiring relating to work done in any work area
shall comply with the materials and methods requirements of Chapters 34 through 43.
Exception: Electrical equipment and wiring in newly installed partitions and
ceilings shall comply with the applicable requirements of Chapters 34 through 43.
AJ501.5.2 Electrical service.
Service to the dwelling unit shall be not less than 100 ampere, three-wire capacity and
service equipment shall be dead front having no live parts exposed that could allow
accidental contact. Type “S" fuses shall be installed where fused equipment is used.
Exception: Existing service of 60 ampere, three-wire capacity, and feeders of 30
ampere or larger two- or three-wire capacity shall be accepted if adequate for the
electrical load being served.
Critical to my evaluation is to understand what is required in association with each of these options. Unlike the repair and renovation options, both alteration and reconstruction require (amongst other things) that electrical services meet certain minimums. See sections AJ501.5.1 and AJ501.5.2 below. The cabin presently does not have any electrical service, and I'd say it would be prohibitively expensive and/or impractical to connect to the street nearly 2 miles away. I do not intend or wish to install an electrical service, as this is a primitive cabin. If I am going to perform an alteration or a reconstruction, do I need to install electrical service? AJ501.5.1 refers to "Newly installed electrical equipment...shall comply...". If there is no electrical equipment being serviced, is it fair to conclude that the provisions related to electrical equipment and wiring (including service to the dwelling unit) do not apply? As an alternative option, would it be possible to comply with these provisions through the installation of a generator?
Thanks in advance for any advice or suggestions,
Al
AJ501.5.1 Materials and methods.
Newly installed electrical equipment and wiring relating to work done in any work area
shall comply with the materials and methods requirements of Chapters 34 through 43.
Exception: Electrical equipment and wiring in newly installed partitions and
ceilings shall comply with the applicable requirements of Chapters 34 through 43.
AJ501.5.2 Electrical service.
Service to the dwelling unit shall be not less than 100 ampere, three-wire capacity and
service equipment shall be dead front having no live parts exposed that could allow
accidental contact. Type “S" fuses shall be installed where fused equipment is used.
Exception: Existing service of 60 ampere, three-wire capacity, and feeders of 30
ampere or larger two- or three-wire capacity shall be accepted if adequate for the
electrical load being served.