Dave L.
REGISTERED
I have a set of plans that show 2 man doors in a bathroom leading to the elevator shaft of a 2 story B occupacy building. Basically, on the back side of the elevator shaft on the 1st floor. I have not seen this before and reached out to the design professional. I reference §BC713.7.1 Prohibited openings Openings other than those necessary for the purpose of the shaft shall not be permitted in shaft enclosures.
They responded back that the doors leading to the back side of the shaft through the men's room are necessary for service and maintenace and will have the same fire rating as the shaft. In addition the doors will be connected to the alarm system and you will not be able to pen them, other than service personell.
This sounds reasonable and does not appear to be a violation.
They responded back that the doors leading to the back side of the shaft through the men's room are necessary for service and maintenace and will have the same fire rating as the shaft. In addition the doors will be connected to the alarm system and you will not be able to pen them, other than service personell.
This sounds reasonable and does not appear to be a violation.