• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Elevator accessible M.O.E. at 4 story bldg, or 5?

Yikes

Gold Member
Joined
Nov 2, 2009
Messages
3,065
Location
Southern California
CBC 1009.2.1 requires an elevator (on emergency power) as an accessible means of egress for accessible floors levels "four or more stories above or below a level of exit discharge".
Help me do the math: if I have a 4 story building on-grade, the 4th floor is actually 3 levels above the level of exit discharge, correct?
So this would typically apply only to 5+ story buildings - - not 4 story buildings, correct?