And 713.4 explicitly says mezzanines don't count.
thats not what it says
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
And 713.4 explicitly says mezzanines don't count.
you trying to get all the AHJs here fired?
Maybe I'm the idiot because I'm not familiar with the US code process. So, when something is added to the code, there is a reason right? In our system, each code change is accompanied with a document like this: https://cbhcc-cchcc.ca/eng/public-review/2025_1/2025-proposed-changes-to-nbc-combined-file-2025-01-15.pdf.Prescriptive requirements should be worded clearly enough so that complete understanding of the intent is not required in order to determine compliance.
In this case the wording used in 713.4 would require a 1 hour fire rating. If the intention was to exempt mezzanine floors from Section 713, that belongs in 713.1. The guidance in 713.4 is just provided for choosing between the two cases of a 1 hour fire rating and a 2 hour fire rating.
Cheers, Wayne
Prescriptive requirements should be worded clearly enough so that complete understanding of the intent is not required in order to determine compliance.
In this case the wording used in 713.4 would require a 1 hour fire rating. If the intention was to exempt mezzanine floors from Section 713, that belongs in 713.1. The guidance in 713.4 is just provided for choosing between the two cases of a 1 hour fire rating and a 2 hour fire rating.
Cheers, Wayne
The number of stories connected by the shaft enclosure shall include any basements
but not any mezzanines.
713.4 Fire-resistance rating. Shaft enclosures shall have a
fire-resistance rating of not less than 2 hours where connecting
four stories or more, and not less than 1 hour where
connecting less than four stories. The number of stories
connected by the shaft enclosure shall include any basements
but not any mezzanines. Shaft enclosures shall have a
fire-resistance rating not less than the floor assembly penetrated,
but need not exceed 2 hours. Shaft enclosures shall
meet the requirements of Section 703.2.1.1.
thats not what it says
The number of stories connected by the shaft enclosure shall include any basements
but not any mezzanines.
You might be right about the intent (beyond my knowledge), but we can say unequivocally that "less than four" includes one and zero.My interpretation (which, obviously, I think is consistent with both the letter and the intent of the code) is that "less than four" means "two or three."
It could be plainer by saying that for 2 or 3 stories, a 1 hour rating is required, and for 4 or more stories a 2 hour rating is required. That implies that for 1 story, no rating is required, but even that could be explicitly stated.It says, right there, that a 1-hour rating is required when connecting less than four stories. And immediately after that it states that "The number of stories connected by the shaft enclosure shall include any basements but not any mezzanines." I don't know how it can be any plainer -- in considering how many stories a shaft connects, we don't count mezzanines.