'21 IBC 3006.2 would NOT require hoistway protection in a 4 story, sprinklered R2 building because it has an NFPA 13 sprinkler system (condition #1). If it did then 3006.3 would tell us how to provide that protection, but there would be an exception for the level of exit discharge. However since this is an R2, 3006.2.1 is the charging language and sends us directly to 3006.3, bypassing 3006.2 and the exception for the level of exit discharge. Since 3006.3 has no exception for the level of exit discharge am I to take it that this is purposeful and that an elevator that opens to an R2 corridor must have a lobby, pressurization or additional doors at the level of exit discharge? That is the way I see it, but apparently not the architect.
I am sure I have encountered this before but I can't recall whether I was right or wrong.