1994 UBC 3002 required elevator lobbies to have at least one exit.
2012 IBC 713.14.1 requires elevator lobbies to have at least one means of egress.
Do either or both of these sections require that an exit stair in a high rise be provided direct access from within the lobby itself? Or could leaving the lobby, travelling down a corridor to an exit stair comply?
Also
2012 IBC 403.6.1 requires a fire service access elevator be installed if occupied floor above 120' (this building exceeds that) and IBC 3007.7 requires those fire service access elevators to open into a fire service access elevator lobby per 713.14.1 (1-hr fire partition) with direct access to an interior exit stairway (3007.7.1) and be enclosed by a 1-hr smoke barrier (3007.7.2) with 45-min doors that are smoke protected (3007.7.3).
So does this section require the elevator lobby/fire service elevator lobby to have DIRECT access to an interior stair from within the lobby?
My situation is this: I have an existing sprinklered high rise built under the 94 UBC with rated corridors. Work proposed on the 16th floor. It has an elevator lobby, enclosed by horizontal sliding doors but has no fire service access elevator lobby and no stair access from within the lobby. A request has been made to "de-rate" the corridors based on the fact that the 2012 IBC 1018 wouldn't require them but I am concerned that the elevator lobbies do not meet the code for having an exit by either 713.14.1 or 3007.7 and the way I see it all applicable elements of the 2012 code would need to be met in order to allow compliance with the current code as opposed to the 94 code. IEBC not in use.
2012 IBC 713.14.1 requires elevator lobbies to have at least one means of egress.
Do either or both of these sections require that an exit stair in a high rise be provided direct access from within the lobby itself? Or could leaving the lobby, travelling down a corridor to an exit stair comply?
Also
2012 IBC 403.6.1 requires a fire service access elevator be installed if occupied floor above 120' (this building exceeds that) and IBC 3007.7 requires those fire service access elevators to open into a fire service access elevator lobby per 713.14.1 (1-hr fire partition) with direct access to an interior exit stairway (3007.7.1) and be enclosed by a 1-hr smoke barrier (3007.7.2) with 45-min doors that are smoke protected (3007.7.3).
So does this section require the elevator lobby/fire service elevator lobby to have DIRECT access to an interior stair from within the lobby?
My situation is this: I have an existing sprinklered high rise built under the 94 UBC with rated corridors. Work proposed on the 16th floor. It has an elevator lobby, enclosed by horizontal sliding doors but has no fire service access elevator lobby and no stair access from within the lobby. A request has been made to "de-rate" the corridors based on the fact that the 2012 IBC 1018 wouldn't require them but I am concerned that the elevator lobbies do not meet the code for having an exit by either 713.14.1 or 3007.7 and the way I see it all applicable elements of the 2012 code would need to be met in order to allow compliance with the current code as opposed to the 94 code. IEBC not in use.