In a 2-story building with 1-hour rated stair and elevator shafts, we know that 60 minute doors are required on stairways from the chart 715.4 as they are in a shaft.
The question is if the elevator machine room for a room that abuts the elevator shaft needs a 45 or 60 minute door?
3006.4 states that if the machine room abuts the hoistway the room shall have the same rating as the elevator shaft.
Does the answer to the question lie solely in weather or not there are unprotected openings between the machine room and hoistway, therefore the machine room is inherently part of the shaft?