Sifu
SAWHORSE
- Joined
- Sep 3, 2011
- Messages
- 3,318
I have an elevator machine room that is not rated as a one hour fire barrier. The room is adjacent to the shaft. It is a two story B occupancy, type V (I think). The elevator is not part of the MOE except for accessibility. Working out of 2009 IBC, section 3006.4 requires the room to be a fire barrier unless it does not abut the shaft. Therefore, from what I know it must be a fire barrier. I discussed this with the superintendent and he agrees....., Today I got an email from the PM and architect claiming that the room did not need a rated fire barrier because the elevator company specs say it is not required. In addition to that, apparently our former plans examiner agreed but unfortunately he is a former plans examiner and I can't ask him. I have great respect for his knowledge so I am now wondering what I don't know. I have requested the "specs" that indicate no fire barrier is required but wonder if any of you learned folks have any input that will shed some light for me. Do the "specs" over-ride the code for this??? BTW, the room has a frameless double swing door (like a kitchen door) and an air transfer grill to the adjacent riser room and an electrical closet, it is otherwise constructed as a 1hr fire barrier.