I have a three story apartment building just finishing up and the elevator company was installing the rails yesterday and they questioned the sheetrock on the interior - in lieu of using metal studs and shaftwall liner panels, we did 2x6 wall framing with two 1/2" layers type X sheetrock on the inside of shaft, 5 1/2" mineral wool insulation and 5/8" type x on the outside - the installer said that they usually see double 5/8, not 1/2"? even though the construction is a-symmetrical, it still has a one hour rating, is there something I'm overlooking here? the interior sheetrock is obviously continuous and the only penetration of the exterior layer is the subfloor, we have fire hangers for the floor joists that connect to the shaft, so essentially continuous as well