For the 2015 IBC I don't believe...no I am wondering if you can cite where both openings and penetrations protection are required for <3 stories shaft enclosure.
Section 713.14 & Section 3002.1 only references requirement to comply with Section 713, no protective requirement is established.
Section 713 only applies to shafts required to protect openings and penetrations through floor/ceiling and roof/ceiling assemblies.
Prefer 2015IBC for hoistway. 2012IBC discussion creates continuous loop
2015IBC
SHAFT. An enclosed space extending through one or more stories of a building, connecting vertical openings in successive floors, or floors and roof.
SHAFT ENCLOSURE. The walls or construction forming the boundaries of a shaft.
713.1 General. The provisions of this section shall apply to shafts required to protect openings and penetrations through floor/ceiling and roof/ceiling assemblies.
713.14 Elevator, dumbwaiter and other hoistways.
Elevator, dumbwaiter and other hoistway enclosures shall be constructed in accordance with Section 713 and Chapter 30.
3002.1 Hoistway enclosure protection. Elevator, dumb-waiter and other hoistway enclosures shall be shaft enclosures complying with Section 713.
There is no discussion when the “and” is ignored. Why rate a shaft when there are no opening protectives (OP thought)