Here is the 2015 IBC takeaway for 2 story elevator shaft enclosure discussion:
1) Elevator hoistways are “shaft enclosures”, see 3002.1
2) “Shaft enclosure” protection applicable only if openings and penetration require protection, see 713.1
3) <3 story no opening protection required, see 3006.2
4) <3 story, 713 not applicable, see 2) above
5) <3 story 713.4 rating not applicable see 2) & 3) above
6) Also refer to 3006.2 for the 5 unique conditions and follow through requirements with Chapter 6 for element ratings of building classification.
Please consider the following “little banter” items that should be ignored:
a) ‘unenclosed elevator’ no such bird
b) ‘1.5hr elevator door’ no such bird, table 716.5 not applicable to elevator doors
c) ‘1hr elevator door’ no such bird, table 716.5 not applicable to elevator doors
d) 712.1.9 is not applicable to elevator hoistways, only 712.1.1 applicable - no exception.
e) ‘1hr door assembly without smoke and draft control’ no such bird in 2015
f) ‘716.5 rating for elevator door requirement’, no such requirement, 716.5 N/A for elevator door
g) “20-min doors in corridors are required to have smoke and draft control as required by Section 716.5.3, as well as doors in smoke barriers; but smoke and draft control is not required for opening protectives in other fire-resistance-rated assemblies unless required by another specific provision” Wrong, all fire door assemblies require NFPA 105 smoke & draft control, so totally disregard the aforementioned statement.
h) "elevator is not required to be in an enclosure" Wrong, see 3002.1
For clarification:
A “shaft enclosure” can be non-rated
A “shaft” is not a “shaft enclosure”
A “fire door” is not a “fire door assembly”
For reference:
SHAFT. An enclosed space extending through one or more stories of a building, connecting vertical openings in successive floors, or floors and roof.
SHAFT ENCLOSURE. The walls or construction forming the boundaries of a shaft.
FIRE DOOR. The door component of a fire door assembly.
FIRE DOOR ASSEMBLY. Any combination of a fire door, frame, hardware and other accessories that together provide a specific degree of fire protection to the opening.
Respect RLGA interpretations, respect that we basically are posting the same conclusions. The problem here is a pathway for conclusion not supported by code - which I can agree to disagree. This however is not acceptable conclusion for a discussion to determine code requirements, determining life safety requirements. This board’s purpose is to crystallize code requirements and eliminate gray areas into a black/white enlightenment of life safety. Yes....your posts are serving a higher purpose.
1) Elevator hoistways are “shaft enclosures”, see 3002.1
2) “Shaft enclosure” protection applicable only if openings and penetration require protection, see 713.1
3) <3 story no opening protection required, see 3006.2
4) <3 story, 713 not applicable, see 2) above
5) <3 story 713.4 rating not applicable see 2) & 3) above
6) Also refer to 3006.2 for the 5 unique conditions and follow through requirements with Chapter 6 for element ratings of building classification.
Please consider the following “little banter” items that should be ignored:
a) ‘unenclosed elevator’ no such bird
b) ‘1.5hr elevator door’ no such bird, table 716.5 not applicable to elevator doors
c) ‘1hr elevator door’ no such bird, table 716.5 not applicable to elevator doors
d) 712.1.9 is not applicable to elevator hoistways, only 712.1.1 applicable - no exception.
e) ‘1hr door assembly without smoke and draft control’ no such bird in 2015
f) ‘716.5 rating for elevator door requirement’, no such requirement, 716.5 N/A for elevator door
g) “20-min doors in corridors are required to have smoke and draft control as required by Section 716.5.3, as well as doors in smoke barriers; but smoke and draft control is not required for opening protectives in other fire-resistance-rated assemblies unless required by another specific provision” Wrong, all fire door assemblies require NFPA 105 smoke & draft control, so totally disregard the aforementioned statement.
h) "elevator is not required to be in an enclosure" Wrong, see 3002.1
For clarification:
A “shaft enclosure” can be non-rated
A “shaft” is not a “shaft enclosure”
A “fire door” is not a “fire door assembly”
For reference:
SHAFT. An enclosed space extending through one or more stories of a building, connecting vertical openings in successive floors, or floors and roof.
SHAFT ENCLOSURE. The walls or construction forming the boundaries of a shaft.
FIRE DOOR. The door component of a fire door assembly.
FIRE DOOR ASSEMBLY. Any combination of a fire door, frame, hardware and other accessories that together provide a specific degree of fire protection to the opening.
Respect RLGA interpretations, respect that we basically are posting the same conclusions. The problem here is a pathway for conclusion not supported by code - which I can agree to disagree. This however is not acceptable conclusion for a discussion to determine code requirements, determining life safety requirements. This board’s purpose is to crystallize code requirements and eliminate gray areas into a black/white enlightenment of life safety. Yes....your posts are serving a higher purpose.