imhotep
Silver Member
2009 IBC
Elevator serving three stories.
Per 708.2 a shaft is required and shall be constructed as fire barriers in accordance with Section 707. Per 708.14.1 an enclosed elevator lobby is not required (three stories). 708.4 requires 1 hour fire-resistance rated construction. 708.7 requires openings in a shaft enclosure to be protected in accordance with Section 715 as required for fire barriers. 715.4 requires a 1 hour fire door assembly.
1 hour shaft walls provided. Per the manufacturer the elevator door carry a 1 1/2 hour fire rating.
Question:
If the shaft opens into a corridor with a 0 hour rating (table 1018.1 B occupancy - sprinkled) is there a requirement to control drafts and the passage of smoke at the protected shaft opening? Is 715.4.3 applicable since the corridor is not rated?
Elevator serving three stories.
Per 708.2 a shaft is required and shall be constructed as fire barriers in accordance with Section 707. Per 708.14.1 an enclosed elevator lobby is not required (three stories). 708.4 requires 1 hour fire-resistance rated construction. 708.7 requires openings in a shaft enclosure to be protected in accordance with Section 715 as required for fire barriers. 715.4 requires a 1 hour fire door assembly.