2 story building, 4,500 SF footprint. both floors have grade access. interior stair connecting the two floors. CT
Owner was told by the B.O. he doesn't need an elevator. I spoke in depth with the B.O. and he cited that he would use 1103.2.2 employee work area exemption to get out of installation of an elevator. He would call the entire floor as an exemption to chapter 11 and only needing to comply with 907.5.2.3.1, 1009 and 1104.3.1.
I suggested that the entire floor being over 3,000 SF, and containing a primary function including loading/unloading work vehicles, storage, toilets etc. would mean its an accessible story that might have portions of the area as employee work areas, but that the employee work area would not exempt the entire 4,500 SF of the floor from being accessible. the offices are all on the upper level. This place is a small contractors office in which employees park the vehicles in, load them with tools, materials etc, receive deliveries of supplies, and minor vehicle maintenance.
I see most of section 1104 as a problem to not having an elevator, or ramps or something.
I can not find a place to clearly show the B.O. that the entire floor can't just be called an employee work area because he told a local business that they don't need an elevator.
any comments or thoughts would be helpful.
Thank you.
Owner was told by the B.O. he doesn't need an elevator. I spoke in depth with the B.O. and he cited that he would use 1103.2.2 employee work area exemption to get out of installation of an elevator. He would call the entire floor as an exemption to chapter 11 and only needing to comply with 907.5.2.3.1, 1009 and 1104.3.1.
I suggested that the entire floor being over 3,000 SF, and containing a primary function including loading/unloading work vehicles, storage, toilets etc. would mean its an accessible story that might have portions of the area as employee work areas, but that the employee work area would not exempt the entire 4,500 SF of the floor from being accessible. the offices are all on the upper level. This place is a small contractors office in which employees park the vehicles in, load them with tools, materials etc, receive deliveries of supplies, and minor vehicle maintenance.
I see most of section 1104 as a problem to not having an elevator, or ramps or something.
I can not find a place to clearly show the B.O. that the entire floor can't just be called an employee work area because he told a local business that they don't need an elevator.
any comments or thoughts would be helpful.
Thank you.