• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Enclosure under interior stairways

VLADIMIR LEVIN

REGISTERED
Joined
Jun 11, 2019
Messages
143
Location
NY
Can someone clarify section 1011.7.3 BCNYS.
I have a metal stair with a utility closet underneath it.
I think the closet walls need to be 1 hour, and the underside of the stair needs to be 1 hour?
 
IBC 101.7.3 says the same thing but also requires it to be at lease the same fire -rated construction as the stairway encloser and the access to the enclosed space cannot be directly from within the stairway encloser.
 

1011.7.3 Enclosures Under Interior Stairways


The walls and soffits within enclosed usable spaces under enclosed and unenclosed stairways shall be protected by 1-hour fire-resistance-rated construction or the fire-resistance rating of the stairway enclosure, whichever is greater. Access to the enclosed space shall not be directly from within the stairway enclosure.

The language seems clear. If the space beneath the stair is enclosed and used as a closet, the enclosure has to be one-hour rated, including the soffit (the celing of the closet).

I agree with your opening assessment.
 
The language seems clear. If the space beneath the stair is enclosed and used as a closet, the enclosure has to be one-hour rated, including the soffit (the celing of the closet).

I agree with your opening assessment.
Do you know a UL assembly for the underside of the stair, or can i just spray it with intumescent paint?
 
If you have 2 by stringers you can use Gypsum Association FC 5406. It requires 2 layers of 5/8" Type X gypsum board, and the ceiling provides 1 hour protection for the joists. FC 5407 & FC 5408 are the same, except for I-joists or trusses.
 
If you have 2 by stringers you can use Gypsum Association FC 5406. It requires 2 layers of 5/8" Type X gypsum board, and the ceiling provides 1 hour protection for the joists. FC 5407 & FC 5408 are the same, except for I-joists or trusses.
Those numbers are not in GA 600-2021 (I don't have the 2024), but FC 5529 appears to be a similar generic assembly for 2x framing. Of course the building code will determine the applicable edition.
 
Yes, you understood correctly. If it is a storage cupboard under an internal staircase, then according to section 1011.7.3 BCNYS, a 1-hour fire protection degree is required for the partitions and for the underside of the staircase. I have already seen it required in inspection.

 
Last edited:
Those numbers are not in GA 600-2021 (I don't have the 2024), but FC 5529 appears to be a similar generic assembly for 2x framing. Of course the building code will determine the applicable edition.

Interesting. FC-5406 was in the 2003 edition, and it had a bold-faced note that the 2 layers of GWB provided 1-hour protection for the joists.

1752948532859.png
 
Back
Top