steveray
SAWHORSE
Any thoughts on whether or not a wood framed equipment platform is allowed in a IIB building? What about a wood structure that stuff hangs off of?
I imagine they are going to argue that it is not a floor and I will argue it is and I will win...But it got me thinking that if it were a "superstructure" that they just wanted to hang stuff off of, would I have to allow it....?
Lets say they want to build a cleanroom with CFMF walls and a wooden truss system to support the gasketed hung ceiling....The trusses are not a floor, they are not a roof, they are not a partition...So they don't fit nicely into T601...603 is really a modifier to T601 IMO, and that situation is not really addressed, which could be grounds for disallowing...Maybe...
So to answer my own question, for platforms, no, per 410.3 anyway, but if it is not actually a platform it would seem to get weird...
505.3
Equipment platforms in buildings shall not be considered as a portion of the floor below. Such equipment platforms shall not contribute to either the building area or the number of stories as regulated by Section 503.1. The area of the equipment platform shall not be included in determining the fire area in accordance with Section 903. Equipment platforms shall not be a part of any mezzanine and such platforms and the walkways, stairways, alternating tread devices and ladders providing access to an equipment platform shall not serve as a part of the means of egress from the building.I imagine they are going to argue that it is not a floor and I will argue it is and I will win...But it got me thinking that if it were a "superstructure" that they just wanted to hang stuff off of, would I have to allow it....?
Lets say they want to build a cleanroom with CFMF walls and a wooden truss system to support the gasketed hung ceiling....The trusses are not a floor, they are not a roof, they are not a partition...So they don't fit nicely into T601...603 is really a modifier to T601 IMO, and that situation is not really addressed, which could be grounds for disallowing...Maybe...
So to answer my own question, for platforms, no, per 410.3 anyway, but if it is not actually a platform it would seem to get weird...