An equipment platform and second means of egress question. IBC 2009 basis.
We have an industrial project that would fall under the F-2, Low Hazard occupancy classification. IIB construction. No sprinkler system.
The 80 foot tall building will house large pieces of equipment related to the pollution control at power generation facilities. There are no permanently, occupied spaces such as control rooms, offices, breakrooms, restrooms, etc. You just have the equipment which is attended to periodically.
Around the equipment you have a series of platforms, mostly metal grating with a few concrete slabs. These platforms are used solely to maintain the equipment. Access to these maintenance platforms is by a single, unenclosed, 36” wide scissors stair with complaint guards, handrails and landings. Travel distance is within the 300 feet allowed. We are also supplying fire escape ladders (NFPA 101 7.9.2.1(3)) as a second means of egress from platforms larger than 300 SF.
The issue we are running into is that the aggregate area of all the equipment platforms is greater than two-thirds of the floor area of the building. (505.5.1) Are they now considered floors/stories? I’m having a difficult time wrapping my head around these unoccupied (by IBC definition) equipment platforms now having to be classified as something else.
The other question is we were just supplying a single stair as an access to these platforms. Would there now be a second stair requirement?
Thanks in advance.
We have an industrial project that would fall under the F-2, Low Hazard occupancy classification. IIB construction. No sprinkler system.
The 80 foot tall building will house large pieces of equipment related to the pollution control at power generation facilities. There are no permanently, occupied spaces such as control rooms, offices, breakrooms, restrooms, etc. You just have the equipment which is attended to periodically.
Around the equipment you have a series of platforms, mostly metal grating with a few concrete slabs. These platforms are used solely to maintain the equipment. Access to these maintenance platforms is by a single, unenclosed, 36” wide scissors stair with complaint guards, handrails and landings. Travel distance is within the 300 feet allowed. We are also supplying fire escape ladders (NFPA 101 7.9.2.1(3)) as a second means of egress from platforms larger than 300 SF.
The issue we are running into is that the aggregate area of all the equipment platforms is greater than two-thirds of the floor area of the building. (505.5.1) Are they now considered floors/stories? I’m having a difficult time wrapping my head around these unoccupied (by IBC definition) equipment platforms now having to be classified as something else.
The other question is we were just supplying a single stair as an access to these platforms. Would there now be a second stair requirement?
Thanks in advance.