EugeneNinniePEAIA
REGISTERED
I have an existing 6200 sq.ft. 80 year old ( the majority sq.ft. of S-1 with small apartment R approx. 800 sq.ft.) 1 story Non Sprinklered Type Vb Construction that has had structural remedial work done to it that is over 50% of the building area. I inspected it and the structural work is satisfactory, however an existing apartment exists off the back contiguous to the S-1 area. Since the work is well over 50% of the building area, the building must be brought up to IBC 2024 standards one of them being the fire separation between S-1 and the Apartment R. On Table 508.4 Required Separation of Occupancies (hours) S-1 and R requires a 2 hr. separation. The client is upset that a 2-hour wall is needed and "feels" it is excessive. There is no building inspector in this county, so it is the wild west. I am not responsible for "feelings" BUT as a PE and Architect it is my professional stamp that goes on it and therefore the 2 hr. stays. What is your opinion? So I can provide the client with additional verification from BCF because I am the type that "feelings" have no basis on a black and white issue, so any verification from BCF would be helpful. Thank You.