We're doing a minor tenant improvement to an existing building in California, built around 2000. There is an existing exterior door that has the electrical meter mounted within 6 inches of the strike side of the door, on the exterior. This obviously doesn't comply, as I need 24" clear on the strike side. The door isn't required for exiting, and leads to an employee/delivery area, no public access.
What are my options here? I believe we could qualify for a hardship, as we're already doing other upgrades elsewhere, in order of priority. Other than that, it's either seal up the door, or relocate the panel, correct? Am I missing anything? Sorry for the dumb question, thanks for the help!