ETThompson
SAWHORSE
Hi
We're doing a tenant improvement for a hair/beauty salon in an existing 1-story shell. The project is at grade and all exits lead to the exterior and a public way. The overall space is Business / B use except for a small accessory storage S-2 space. Construction Type is IIB. Overall space is about 11k sf. The project is not sprinkelered. We're under the Ohio Building Code 2017 which follows the 2015 IBC.
The existing build-out (which we're partly keeping), has what appears to be an existing 1-hr corridor. However, our analysis is that because we have (3) exits and all our travel paths are well under our required travel distances (200' feet allowed, our maximum is 115 ft.).
Thus our analysis is that this former "corridor" is not required to be a corridor for our project. (Corridor defined in Ch. 2 as "An enclosed exit access component that defines and provides a path of egress travel"). Are we correct in thinking this is not required to be considered a rated corridor?
The design proposes a couple of large unprotected openings in this former rated corridor (8' long by 6' high interior relight glazing, not fire rated). Our thought is since the corridor is not truly required to be a "corridor", we should be allowed to have these unprotected openings (also, non-rated doors, etc).
I should also mention that this project has been permitted, without adverse comment on the issue above. The concern on a team member's part is the field inspector will raise an objection, and we'd like to confirm that our analysis is correct.
See attached Life Safety plan showing corridor (hm, having trouble attaching file...will do later...). This drawing probably should have been clearer that the existing 1-hr rated corridor was not required for our design, but as I said it was successfully permitted this way...
Thanks
We're doing a tenant improvement for a hair/beauty salon in an existing 1-story shell. The project is at grade and all exits lead to the exterior and a public way. The overall space is Business / B use except for a small accessory storage S-2 space. Construction Type is IIB. Overall space is about 11k sf. The project is not sprinkelered. We're under the Ohio Building Code 2017 which follows the 2015 IBC.
The existing build-out (which we're partly keeping), has what appears to be an existing 1-hr corridor. However, our analysis is that because we have (3) exits and all our travel paths are well under our required travel distances (200' feet allowed, our maximum is 115 ft.).
Thus our analysis is that this former "corridor" is not required to be a corridor for our project. (Corridor defined in Ch. 2 as "An enclosed exit access component that defines and provides a path of egress travel"). Are we correct in thinking this is not required to be considered a rated corridor?
The design proposes a couple of large unprotected openings in this former rated corridor (8' long by 6' high interior relight glazing, not fire rated). Our thought is since the corridor is not truly required to be a "corridor", we should be allowed to have these unprotected openings (also, non-rated doors, etc).
I should also mention that this project has been permitted, without adverse comment on the issue above. The concern on a team member's part is the field inspector will raise an objection, and we'd like to confirm that our analysis is correct.
See attached Life Safety plan showing corridor (hm, having trouble attaching file...will do later...). This drawing probably should have been clearer that the existing 1-hr rated corridor was not required for our design, but as I said it was successfully permitted this way...
Thanks