Mech
REGISTERED
2009 IBC w/ 2012 IBC Chapter 11
2009 ANSI / ICC A117.1
ADA
2000 NFPA 101 - Life Safety Code
I am trying to establish a 30 minute fire rated smoke partition in an existing nursing home to comply with the 2000 Life Safety Code.
Ideally, a non-accessible single user restroom door and wall (not currently rated) would be upgraded to provide part of the fire rated smoke partition. The drawings for this previous renovation are dated January 1990; ADA was not signed into law until later in the year. The only item that might be accessible in this restroom is the light switch. The room is too small (maybe 5' x 4'-6") to relocate either the plumbing fixtures or the door to provide all the necessary clearances.
Can the drywall be changed without requiring the restroom to be made accessible?
Can the existing door and frame be changed without enlarging it to provide 34" clearance when the door is open? I understand the door knobs would be replaced with levers. I think there is sufficient room to install a compliant door, but there will not be adequate maneuvering space inside the restroom.
Can a door closer be added to the door without making the restroom accessible? If not, can an electrically operated door opener / closer be added without making the restroom accessible?
If there were sufficient room to reconstruct the restroom as 100% compliant, I would not be opposed to it.
Thanks
2009 ANSI / ICC A117.1
ADA
2000 NFPA 101 - Life Safety Code
I am trying to establish a 30 minute fire rated smoke partition in an existing nursing home to comply with the 2000 Life Safety Code.
Ideally, a non-accessible single user restroom door and wall (not currently rated) would be upgraded to provide part of the fire rated smoke partition. The drawings for this previous renovation are dated January 1990; ADA was not signed into law until later in the year. The only item that might be accessible in this restroom is the light switch. The room is too small (maybe 5' x 4'-6") to relocate either the plumbing fixtures or the door to provide all the necessary clearances.
Can the drywall be changed without requiring the restroom to be made accessible?
Can the existing door and frame be changed without enlarging it to provide 34" clearance when the door is open? I understand the door knobs would be replaced with levers. I think there is sufficient room to install a compliant door, but there will not be adequate maneuvering space inside the restroom.
Can a door closer be added to the door without making the restroom accessible? If not, can an electrically operated door opener / closer be added without making the restroom accessible?
If there were sufficient room to reconstruct the restroom as 100% compliant, I would not be opposed to it.
Thanks