Code: 2010 California Building Code
Have an assembly area in a fully sprinklered building which, based on table 1004.1.1 would allow for 350 occupants. This area, of course will require at least 2 exits.
Problem: One of the exit paths leads to an area which, because of passage width and additional persons exiting from other rooms, can only allow 50 persons to exit the assembly area in question. (no, I can't reroute any of them) Therefore, if 2 exits are provided and they must be equal, I am limited to an occupancy level of 100.
Question: It is possible to provide 2 additional exits through adjacent spaces (which comply with "intervening spaces" requirements) , can I rate these exit paths at 50 each, thus bringing the space occupancy allowance up to 200?
Have an assembly area in a fully sprinklered building which, based on table 1004.1.1 would allow for 350 occupants. This area, of course will require at least 2 exits.
Problem: One of the exit paths leads to an area which, because of passage width and additional persons exiting from other rooms, can only allow 50 persons to exit the assembly area in question. (no, I can't reroute any of them) Therefore, if 2 exits are provided and they must be equal, I am limited to an occupancy level of 100.