We have an R-2 dorm, two stories at 2,192 sqft per floor. Each floor is a double loaded hall with sleeping rooms and shared baths for both men/women with exit stairs at each end. Because of the per square foot occupant load for a dorm (50 sqft per) the load is 44 per floor, and since we are trying to not have sprinklers in the building this hallway is not permitted to be a corridor. My question is can the hallway be classified as an exit passageway? I think this would prohibit a janitors closet or storage off the exit passageway (or the required drinking fountain?), but all the rooms we are proposing off of the hall are occupied spaces, so my reading was yes. Unless I'm miss reading the restrictions for uses of an exit passageway, any clarification would help.