This is a new R-1 use and it is required to have a smoke detection system installed to notify the occupants.The building does not have an alarm system to connect to Mag Holders
No there are required exits and additional exits. Each required exit has to serve a percentage of the occupant load based on the number of required exits.A 2500 sq ft R-1 has an occupant load of 13 people. The code only requires one exit. This R-1 being on a second floor requires two exits with an exception for one exit by limiting the travel distance to 50 feet to a protected single exit. The open stairs would not be part of the means of egress and therefore code compliant.By Definition, occupant load is the number of persons the means of egress of a building or space is designed to serve; not the number of persons a single exit is expected to serve. Therefore, each exit provided is serving the total occupant load of that area.