Occupant load around 500. I have enough width at the main exit.Does the restaurant have a capacity of over 300 people.
The width of an exterior court is to be determined in
the same fashion as for an interior corridor. The width
is to be not less than that required to serve the number
of occupants from the exit or exits and not less than
the minimum specified in this section (see also Section
1205). The width of the court and any openings
through barriers around the court must be sufficient to
accommodate the number of occupants leaving the
building so that the court will not become a bottleneck
for the egress path.
A cross reference to Section 1005.7 in the exceptions
for width in aisles (see Section 1018.1), corridors
(see Section 1020.4), exit passageways (see Section
1024.2) and exit courts (see Section 1029.2) reinforces
the fact that the protrusion limits provision is
generally applicable for these types of confined routes.
That establishment I would require 10 foot of sidewalk width, plusses consideration of the exit coming in from the sideOccupant load around 500. I have enough width at the main exit.
I agree. and yes I am good on exits. Thank you all for your comments!I think the 10 ft. requirement more for fire separation than exit width. Do you have a third exit if over 500 occupants (IBC Table 1006.3.3)? Do you have adequate separation between exits (IBC 1007)?
Here's the 2021 IBC Commentary on 1029.2:
I think a 2-foot wall constraining the path of exit discharge travel would qualify as a barrier or a "bottleneck." So, without any information suggesting otherwise, my view is that the 2-foot planter has to be considered. The actual width of the walkway should be sized based on the occupant load served. Since this will be an egress court, the next question is whether or not the exterior wall of building along the egress court needs to be fire-resistance rated
I'm confused. The OP referenced 1029.2, but in the 2023 FBC that is 1030.2.
Meanwhile it appears that in post #4, YC quoted the commentary from 1029.2, but I think what we really need is the commentary from 1030.2.
I think the 10 ft. requirement more for fire separation than exit width. Do you have a third exit if over 500 occupants (IBC Table 1006.3.3)? Do you have adequate separation between exits (IBC 1007)?