True. I originally sent sketches asking whether the measurement should be taken parallel to the frame or parallel to the door (see attached) but he kept coming back with the cylinder.Just to clarify...this was the DRAFT, not the final sketch that reflected what the ICC said was the correct way to measure. The link for that is: http://www.ihatehardware.com/?p=3130Clear Width Measurement.jpg[/attachment:354szil2]View attachment 53fw. said:If the door needs to be accessible, I think that instead of a cylinder, a rectangle should be used. Wheelchairs aren't round.
I don't see a direct answer in the landings sections but maybe I'm just missing it:Coug Dad said:for doors that open less than 90 degress the landing provisions of 1008.1.4 and 1008.1.5 (2006) address the issue.
Exactly. I agree with this and what brudgers said.fw. said:If the door needs to be accessible, I think that instead of a cylinder, a rectangle should be used. Wheelchairs aren't round.
Exactly. I agree with this and what brudgers said.TJacobs said:fw. said:If the door needs to be accessible, I think that instead of a cylinder, a rectangle should be used. Wheelchairs aren't round.
Ask him how it complies with A117.1 figure 404.2.3.1LGreene said:Is there anything in the IBC or A117.1 that I can take back to the ICC to see if they want to change their answer? In A117.1-2003 it talks about clear floor space of 30" wide by 48" long in 305.3. If a 30" x 48" or 32" x 48" rectangle is the minimum rather than a 32" diameter cylinder, I'll ask again - if he'll take my call.Thanks for your input everyone.
The photo in the blog post is not the same door that I had the question about. The 50 doors in the college classroom building are stair and corridor doors.Plans Approver said:Wouldn't 1024.2 also be applicable. "The capacity of the exit discharge shall be not less than the required discharge capacity of the exits being served."Can't determine what is on the other side of that door. An occupant load of less than 50 (exit discharge width = 36" wide) or greater than 50 (exit discharge width = 44" wide).
Also the diagram does not match the picture, it should probably look more like this.
![]()
Obviously, existing and not accessible.
Sorry 'bout that. I reverted to college days when I looked at the pictures instead of reading the articles like my classmates.The photo in the blog post is not the same door that I had the question about. The 50 doors in the college classroom building are stair and corridor doors.
I still can't see how the door complies with the clear floor area requirements which show the door at 90 degrees.Plans Approver said:So I put together the following illustrations for a 34 1/2" door which fails to maintain 32" clear at 80 degree opening and a 36" door which fails to maintain 32" clear at approximately 69 degrees.I guess their rationale is that if the door was open 90 degrees it complies with 1008.1.1 etc., and, the accessible clear space of 32" measured perpendicular to the door is maintained.
Based on my knowledge of the group that populates this forum, and my experiences with ICC, I would rely on the members of this board every time.LGreene said:I swear, I love you guys.The rest of the world thinks I'm crazy for thinking about this stuff, and you're taking time out of your busy day to do detailed drawings of various layouts!ICC is sticking with the cylinder method, but I am going to modify my blog post and add the rectangle as another possibility for "testing" the accessibility of the door.
As always, I appreciate all of your insight. Have a great weekend.
- Lori
Sorry 'bout that. I reverted to college days when I looked at the pictures instead of reading the articles like my classmates.Plans Approver said:The photo in the blog post is not the same door that I had the question about. The 50 doors in the college classroom building are stair and corridor doors.
I agree with you as well. I only made the drawings to try to understand why ICC would accept less than 90 degrees. Also at what point ICC's interpretation fails. It's not a good or accurate interpretation by ICC. I have had many of those.John Drobysh said:From Plans Approver... "IBC 1008.1.1, ANSI 117.1, and ADAAG 4.13.5 all state "Clear openings of doorways with swinging doors shall be measured between the face of the door and the stop, with the door open 90 degrees""Personally, I take that to mean the door must open to at least 90 deg in order to comply with 1008.1.1 and the standard(s). Anything less and it cannot be used as an 'exit'. 'Shall' means 'required', 'must', 'mandatory'.
Actually it was texasbo that said..."Based on my knowledge of the group that populates this forum, and my experiences with ICC, I would rely on the members of this board every time."John Drobysh said:P.S. and FWIW, I agree with Jake. This boards membership is far more reliable than ICC for answers.
I disagree with your interpretation of 10081.1.John Drobysh said:From Plans Approver... "IBC 1008.1.1, ANSI 117.1, and ADAAG 4.13.5 all state "Clear openings of doorways with swinging doors shall be measured between the face of the door and the stop, with the door open 90 degrees""Personally, I take that to mean the door must open to at least 90 deg in order to comply with 1008.1.1 and the standard(s). Anything less and it cannot be used as an 'exit'. 'Shall' means 'required', 'must', 'mandatory'.
P.S. and FWIW, I agree with Jake. This boards membership is far more reliable than ICC for answers.