I will try and paint a picture of my scenario in a way that I can get some solid answers. Long narrow two story building. There are three exit stairs. One at each end of the building connected to each other with a corridor. There is a central two story open area with a open stair and elevator smack in the middle of the building/corridor. The building was originally designed to have an occupant load on the floor of more than 500 persons, hence the 3 exit stairs.
Have a tenant that will take the entire end of the building just beyond the atrium. This tenant area will now have one of the exit stairs internal to them and no other tenants will be able to access this stair. This large tenant will exit down their internal stair along with going out the other direction thru the corridor and down the open stair within the two story open area. All exiting travel distances work.
The remaining tenants on the floor all have access to the other enclosed exit stair as well as the open stair in the center thru the rated corridor. Everyone has access to two stairs and all travel distances are in compliance. I do not see an issue with this exiting concept at all.
A fire marshal is insisting that this proposed large tenant cannot capture the one exit stair and make it unavailable for the rest of the tenants on the floor. he quotes this section.
Section 1001.2: It shall be unlawful to alter a building or structure in a manner that will reduce the number of exits or the capacity of the means of egress to less than required by this code. I do not believe what we are proposing creates a situation that is "less than required by this code"
My concern that I would like more clarification on is based upon CBC Table 1006.3.2 "Minimum number of exits or access to exits" for an occupant load of 501- 1000 that requirement is 3. We have 3 stairs. I do not believe that all three stairs need to be available to everyone on the floor, but I cannot find code language that would clarify this.
That are your thoughts?
Have a tenant that will take the entire end of the building just beyond the atrium. This tenant area will now have one of the exit stairs internal to them and no other tenants will be able to access this stair. This large tenant will exit down their internal stair along with going out the other direction thru the corridor and down the open stair within the two story open area. All exiting travel distances work.
The remaining tenants on the floor all have access to the other enclosed exit stair as well as the open stair in the center thru the rated corridor. Everyone has access to two stairs and all travel distances are in compliance. I do not see an issue with this exiting concept at all.
A fire marshal is insisting that this proposed large tenant cannot capture the one exit stair and make it unavailable for the rest of the tenants on the floor. he quotes this section.
Section 1001.2: It shall be unlawful to alter a building or structure in a manner that will reduce the number of exits or the capacity of the means of egress to less than required by this code. I do not believe what we are proposing creates a situation that is "less than required by this code"
My concern that I would like more clarification on is based upon CBC Table 1006.3.2 "Minimum number of exits or access to exits" for an occupant load of 501- 1000 that requirement is 3. We have 3 stairs. I do not believe that all three stairs need to be available to everyone on the floor, but I cannot find code language that would clarify this.
That are your thoughts?