In an R2 occupancy, if the 3rd story has 8 apartments but only 4 of the apartments exit onto that story, can there be only one exit from that story?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Yes. But what is the intent of the this section?. I only have 4 dwelling units exiting on that story.
If the story has more than 4..it needs more than 1....Yes. But what is the intent of the this section?. I only have 4 dwelling units exiting on that story.
I found this:If the story has more than 4..it needs more than 1....
I agree. I reached out to the state for confirmation. Will post back when I get an answerPer § 1006.3.4(1), if the number of units does not EXCEED the number of units listed in Table 1006.3.4(1), then only one exit is required. I would argue that if only four units discharge to that story, only one exit would be required under this section. I would contact the local building official / fire marshal to get confirmation on their interpretation of this section.
Interesting. How do the other 4 apartments exit?I agree. I reached out to the state for confirmation. Will post back when I get an answer