2006 IBC:
Is it the intent of the code writers to mean that Table 602 (fire ratings for exterior walls as based upon separation distance) should override the fire ratings in Table 601/Bearing Walls/Exterior? If so, this is not clearly stated. Section 602.1 clearly says "building elements SHALL HAVE a fire resistance rating NOT LESS than that specified in Table 601 AND exterior walls SHALL HAVE a fire resistance rating NOT LESS than that specified in Table 602.
Suppose I have a Type I-A structure, Table 601 says Bearing Walls/Exterior for Type I-A: 3 hour rating. Footnote "f" adds that I must also be "NOT LESS THAN the fire-resistance rating based on fire separation distance (table 602). Footnote "g" adds "not less than the fire resistance rating as referenced in Section 704.10 When I check Table 602, I see that if I am greater than 30' distance, the rating drops to zero. However, it seems that Table 601 allows a "0 hour" rating only for types II-B, III-B, and V-B construction.
I can think of many instances in the past where a building was judged to be a certain building construction type and then the decision is made to go with a "0-hour" exterior wall because of separation from adjacent structures. I don't see in 602.1 where that determination is allowed. The code says "building elements" (including exterior walls which are listed there in the table) AND exterior walls must meet Table 602. I believe any exterior wall must meet the most stringent of both listings. Am I correct?
Is it the intent of the code writers to mean that Table 602 (fire ratings for exterior walls as based upon separation distance) should override the fire ratings in Table 601/Bearing Walls/Exterior? If so, this is not clearly stated. Section 602.1 clearly says "building elements SHALL HAVE a fire resistance rating NOT LESS than that specified in Table 601 AND exterior walls SHALL HAVE a fire resistance rating NOT LESS than that specified in Table 602.
Suppose I have a Type I-A structure, Table 601 says Bearing Walls/Exterior for Type I-A: 3 hour rating. Footnote "f" adds that I must also be "NOT LESS THAN the fire-resistance rating based on fire separation distance (table 602). Footnote "g" adds "not less than the fire resistance rating as referenced in Section 704.10 When I check Table 602, I see that if I am greater than 30' distance, the rating drops to zero. However, it seems that Table 601 allows a "0 hour" rating only for types II-B, III-B, and V-B construction.
I can think of many instances in the past where a building was judged to be a certain building construction type and then the decision is made to go with a "0-hour" exterior wall because of separation from adjacent structures. I don't see in 602.1 where that determination is allowed. The code says "building elements" (including exterior walls which are listed there in the table) AND exterior walls must meet Table 602. I believe any exterior wall must meet the most stringent of both listings. Am I correct?