Morning all,
I’m working on a code footprint for a wood stake factory (think wood building layout stakes). Currently calling the 7,500 s.f. building F-1/S-1 non separated non sprinklered type VB (IBC 2018). Calling it VB because of some of the wood infill walls -even though it is a PEMB (pre engineered metal building Type II-B)
Question 1 on sprinks 903.2.4.1. “Woodworking operations” says that you have to sprink any area over 2500s.f that generates “finely divided combustible waste”. Is that waste just saw dust or finer dust from sanding? The company does not use any sanding operations and they use a collection system that vacuums shavings and pipes them to outside storage containers. I did see the reference to Chapter 22 of the IFC in the aforementioned IBC 903.2.4.1. The IFC mentions a mandatory DHA (Dust hazard analysis) I am currently looking into that. (the stake company has not done one of those).
Question 2: If I do call the space F-1 or S-1 am I correct in referring back to chart 301.1(1) in finding the maximum allowable quantity for fire area of only 125 pounds(combustible solids)? That’s only a couple sheet of ¾” plywood…. I am envisioning at least a few racks full of raw materials to make stakes with. Seems like an S-1 area should be able to have a lot more than that. Am I not using the chart correctly?
Thanks all,
Mark Schwartzkopf
I’m working on a code footprint for a wood stake factory (think wood building layout stakes). Currently calling the 7,500 s.f. building F-1/S-1 non separated non sprinklered type VB (IBC 2018). Calling it VB because of some of the wood infill walls -even though it is a PEMB (pre engineered metal building Type II-B)
Question 1 on sprinks 903.2.4.1. “Woodworking operations” says that you have to sprink any area over 2500s.f that generates “finely divided combustible waste”. Is that waste just saw dust or finer dust from sanding? The company does not use any sanding operations and they use a collection system that vacuums shavings and pipes them to outside storage containers. I did see the reference to Chapter 22 of the IFC in the aforementioned IBC 903.2.4.1. The IFC mentions a mandatory DHA (Dust hazard analysis) I am currently looking into that. (the stake company has not done one of those).
Question 2: If I do call the space F-1 or S-1 am I correct in referring back to chart 301.1(1) in finding the maximum allowable quantity for fire area of only 125 pounds(combustible solids)? That’s only a couple sheet of ¾” plywood…. I am envisioning at least a few racks full of raw materials to make stakes with. Seems like an S-1 area should be able to have a lot more than that. Am I not using the chart correctly?
Thanks all,