Starting to see more and more of this lately. Automatic failure and redo for both DIY and Pros alike. Anyone do something different? Won't even go to the testing procedure anymore.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
2003 IBC & 2003 IRC and obviously I haven't been enforcing the requirements of the code. We do require testing of waste drains and vents but, that no excuse for my ignorance. Thanks JohnJohn Drobysh said:karmann33 - Yes, you're missing something...2006 IPC 705.14.2 Solvent cementing. (And 2006 IRC at P3003.14.2)
Joint surfaces shall be clean and free from moisture. A purple primer that conforms to ASTM F 656 shall be applied. Solvent cement not purple in color and conforming to ASTM D 2564, CSA B137.3, CSA B181.2 or CSA B182.1 shall be applied to all joint surfaces. The joint shall be made while the cement is wet and shall be in accordance with ASTM D 2855. Solvent-cement joints shall be permitted above or below ground.
What year Code are you using/based on?