Think of it as a KOA campground cabin or tepee that is rented out for a night of sleeping in. Are you sprinkling them?
The requirement to sprinkle all R-1 without some exceptions for a single unit is a big over site. Here is how we handle it in Montana
ernational Building Code shall be the building official.
(12) Delete Subsection 903.2.8 and replace with the following:
"1. An approved automatic sprinkler system installed in accordance with Section 903.3 shall be provided in all Group R buildings meeting any of the following criteria:
"a. 9 or more transient guests or 5 or more transient guestrooms;
"b. 9 or more occupants in other than dwelling units;
"c. 5 or more dwelling units; or
"d. more than 2 stories.
"2. In lieu of the above required automatic sprinkler system in buildings not more than three stories above the lowest level of exit discharge, each transient guestroom may be provided with at least one door leading directly to an exterior exit access that leads directly to approved exits.
"3. "Transient guest" for the purpose of this subsection shall mean an occupant who is primarily transient in nature, staying at one location for 30 days or less."