I am looking an NEC code reference and cannot find it.
So here's the situation: residential service with a disconnect fed to a 200 amp subpanel.
The uninsulated grounding feeder conductor is run to the panel, and put under a lug that is bonded to the enclosure.
The branch circuit grounding conductors are on a ground bar that is bonded to the enclosure.
This means that the grounding path goes through the case of the panel. I am an electrician (and an inspector) and I know this is not a good way to do it, but at the moment, I can't find the code reference one way or the other. Looking for some help!
Thanks.