Yikes
SAWHORSE
California Fire Code 505.3.2.1 says that fire roads must be min. 20' unobstructed width except for security gates per 503.6.
Does that wording (see actual text below) actually allow for security gates in the opened position to have a width smaller than 20'?
We have a client with a project that was approved/built in 1996 with separate 12' wide sliding in-gate and a 12' wide sliding out-gate, separated by a landscape island and fountain. The rest of the roadway is 34' wide.
The owner recently got a permit from the city to delete the landscape island (the fountain was an ugly maintenance hassle), making each new gate almost 17' wide. But the gates are now swinging, and the gate builder also installed a center post section so the gates would be secure against the post in a closed position.
Now, when the gates are fully opened, there is a 17' wide in, and a 17' wide out, separated by an 8" steel post. The new fire inspector is now saying, no, you need a full 26' unobstructed width when the gates are opened.
Here's the actual text of the fire code:
503.2.1 Dimensions. Fire apparatus access roads shall have an unobstructed width of not less than 20 feet (6096 mm), exclusive of shoulders, except for approved security gates in accordance with Section 503.6, and an unobstructed vertical clearance of not less than 13 feet 6 inches (4115 mm).
503.6 Security gates. The installation of security gates across a fire apparatus access road shall be approved by the fire chief. Where security gates are installed, they shall have an approved means of emergency operation. The security gates and the emergency operation shall be maintained operational at all times. Electric gate operators, where provided, shall be listed in accordance with UL 325. Gates intended for automatic operation shall be designed, constructed and installed to comply with the requirements of ASTM F 2200.
Does that wording (see actual text below) actually allow for security gates in the opened position to have a width smaller than 20'?
We have a client with a project that was approved/built in 1996 with separate 12' wide sliding in-gate and a 12' wide sliding out-gate, separated by a landscape island and fountain. The rest of the roadway is 34' wide.
The owner recently got a permit from the city to delete the landscape island (the fountain was an ugly maintenance hassle), making each new gate almost 17' wide. But the gates are now swinging, and the gate builder also installed a center post section so the gates would be secure against the post in a closed position.
Now, when the gates are fully opened, there is a 17' wide in, and a 17' wide out, separated by an 8" steel post. The new fire inspector is now saying, no, you need a full 26' unobstructed width when the gates are opened.
Here's the actual text of the fire code:
503.2.1 Dimensions. Fire apparatus access roads shall have an unobstructed width of not less than 20 feet (6096 mm), exclusive of shoulders, except for approved security gates in accordance with Section 503.6, and an unobstructed vertical clearance of not less than 13 feet 6 inches (4115 mm).
503.6 Security gates. The installation of security gates across a fire apparatus access road shall be approved by the fire chief. Where security gates are installed, they shall have an approved means of emergency operation. The security gates and the emergency operation shall be maintained operational at all times. Electric gate operators, where provided, shall be listed in accordance with UL 325. Gates intended for automatic operation shall be designed, constructed and installed to comply with the requirements of ASTM F 2200.