fire access road
BSSTG
Gold Member
Seadrift, Tx.
Greetings,
2009 IFC states thusly
503.1.1 Buildings and facilities. Approved fire apparatus access roads shall be provided for every facility, building or portion of a building hereafter constructed or moved into or within the jurisdiction. The fire apparatus access road shall comply with the requirements of this section and shall extend to within 150 feet (45 720 mm) of all portions of the facility and all portions of the exterior walls of the first story of the building as measured by an approved route around the exterior of the building or facility.
Exception: The fire code official is authorized to increase the dimension of 150 feet (45 720 mm) where:1. The building is equipped throughout with an approved automatic sprinkler system installed in accordance with Section 903.3.1.1, 903.3.1.2 or 903.3.1.3.
The wording in this section confounds me. When the Code states that access roads shall extend to within 150' would the following be allowed?
Fire rd runs the full length of a strip center on the front side. Strip center is 200' long by 100' wide. Since the rear portions of the building are not farther than the 150' minimum required from the access road, it seems to me that this would be compliant. I feel relatively certain that this is the intent. Would you agree? It may sound like a silly question but we have an issue with a revised site plan (after plan approval) and it's a bit of a pain.
thanksabunch
BSSTG
Regardless of the 150 ft. dimension, if the fire department responds
on the front side of your Strip Center, can they reach all areas of the
roofs for fire fighting, ...water coverage, ...possible ingress, ...possibly
attentioning elec. meter disconnections, ...Siamese Connection,
...parking lot traffic management, ...other ? :-o
Also, while the 100' width may not seem all that long of a distance to
some, ...it may be a whole other issue if you are the one on that
Apparatus ladder about 25 ft. - 35 ft. in the air, or even navigating
that roof on foot, ...in full gear, ...with a 2 in. - 3 in. hose full of water
dragging it around.
Just sayin', ...that rear access road might look pretty good by now!
In the FWIW Dept., ...a lot of Strip Centers are designed and built to
look good, not necessarily to be functional & accessible by the
emergency responding community, nor truck drivers. :banghd
""" of all portions of the facility """
1. Some people go by your example. I can walk from the front where the fire truck parks to through the building to the back, and it is not over 150.
2. I have been use to ,,, where you park the fire truck you must be able to stretch the hose to all portions of the exterior of the building, with out walking through the building....
So I would not approve your example
The answer is quite clear in the code
Not approved
A 20,000 sq ft mercantile should be sprinklered. Now from the left and right front corners you would need to drag the hose 200 ft to reach the entire length of the rear of the building. The exception permits the FO to approve the additional distance. Yes it can be approved however I would document the reason why
Soooo.....you can't have a firewall longer than 150'? Wthout special approval? Because it is the exterior of the building...Or a building wider than 300?....Bad wording...
I think i understand your question
It is a matter how the section is interpreted
