BSSTG
Gold Member
Greetings,
2009 IFC states thusly
503.1.1 Buildings and facilities. Approved fire apparatus access roads shall be provided for every facility, building or portion of a building hereafter constructed or moved into or within the jurisdiction. The fire apparatus access road shall comply with the requirements of this section and shall extend to within 150 feet (45 720 mm) of all portions of the facility and all portions of the exterior walls of the first story of the building as measured by an approved route around the exterior of the building or facility.
Exception: The fire code official is authorized to increase the dimension of 150 feet (45 720 mm) where:1. The building is equipped throughout with an approved automatic sprinkler system installed in accordance with Section 903.3.1.1, 903.3.1.2 or 903.3.1.3.
The wording in this section confounds me. When the Code states that access roads shall extend to within 150' would the following be allowed?
Fire rd runs the full length of a strip center on the front side. Strip center is 200' long by 100' wide. Since the rear portions of the building are not farther than the 150' minimum required from the access road, it seems to me that this would be compliant. I feel relatively certain that this is the intent. Would you agree? It may sound like a silly question but we have an issue with a revised site plan (after plan approval) and it's a bit of a pain.
thanksabunch
BSSTG
2009 IFC states thusly
503.1.1 Buildings and facilities. Approved fire apparatus access roads shall be provided for every facility, building or portion of a building hereafter constructed or moved into or within the jurisdiction. The fire apparatus access road shall comply with the requirements of this section and shall extend to within 150 feet (45 720 mm) of all portions of the facility and all portions of the exterior walls of the first story of the building as measured by an approved route around the exterior of the building or facility.
Exception: The fire code official is authorized to increase the dimension of 150 feet (45 720 mm) where:1. The building is equipped throughout with an approved automatic sprinkler system installed in accordance with Section 903.3.1.1, 903.3.1.2 or 903.3.1.3.
The wording in this section confounds me. When the Code states that access roads shall extend to within 150' would the following be allowed?
Fire rd runs the full length of a strip center on the front side. Strip center is 200' long by 100' wide. Since the rear portions of the building are not farther than the 150' minimum required from the access road, it seems to me that this would be compliant. I feel relatively certain that this is the intent. Would you agree? It may sound like a silly question but we have an issue with a revised site plan (after plan approval) and it's a bit of a pain.
thanksabunch
BSSTG