I have an existing, 3-story office building. Total occupant load is about 415 with 140 occupants each on the 2nd and 3rd floors. the first floor is being renovated for a new tenant; no additional square footage is being added to the building. There is no renovation work on the 2nd and 3rd floors. The building is sprinklered throughout (NFPA 13), but there is no fire alarm system.
2006 IFC Section 907.3 does not require a fire alarm system to be retroactively installed in Group B buildings. The fire marshal is stating that, since almost the entire first floor is being renovated, this is "new construction" and that the entire building has to be retrofitted with a fire alarm system. Section 907.2 in the IBC and IFC is for new "buildings and sructures," so I assume he's applying this section because the renovation is a new "structure" by the IBC definition.
However, Chapter 34 of the IBC only requires compliance to the requirements for new construction for the alternation, and not the entire building. Therefore, only the first floor should be required to have a fire alarm installed.
Would a fire alarm be required throughout the existing building or just the first floor? Or, is IFC Section 907.3 applicable since the entire building isn't undergoing alteration?
Thanks.
2006 IFC Section 907.3 does not require a fire alarm system to be retroactively installed in Group B buildings. The fire marshal is stating that, since almost the entire first floor is being renovated, this is "new construction" and that the entire building has to be retrofitted with a fire alarm system. Section 907.2 in the IBC and IFC is for new "buildings and sructures," so I assume he's applying this section because the renovation is a new "structure" by the IBC definition.
However, Chapter 34 of the IBC only requires compliance to the requirements for new construction for the alternation, and not the entire building. Therefore, only the first floor should be required to have a fire alarm installed.
Would a fire alarm be required throughout the existing building or just the first floor? Or, is IFC Section 907.3 applicable since the entire building isn't undergoing alteration?
Thanks.