Francis Vineyard
REGISTERED
The commentary agrees with the accessibility provision with aggregate floor area but not true for the sprinklers.
"Enclosed areas such as retail areas, press boxes and concession stands require sprinklers if they are in excess of 1,000 square feet (93 m2). The 1,000- square-foot (93 m2) accessory use area is not intended to be an aggregate condition but rather per space. Thus, a press box that is 2,500 square feet (232 m2) in area would need to be subdivided into areas less than 1,000 square feet (93 m2) each in order to be below the threshold for sprinklers. There is no specific requirement for the separation of these spaces. It is assumed, however, that the separation would be a solid barrier of some type but without a required fire-resistance rating. The provision is meant to mirror that in Section 1028.6.2.3, which exempts press boxes and storage facilities less than 1,000 square feet (93 m2) in area from sprinkler requirements in smoke-protected assembly seating areas."
"Enclosed areas such as retail areas, press boxes and concession stands require sprinklers if they are in excess of 1,000 square feet (93 m2). The 1,000- square-foot (93 m2) accessory use area is not intended to be an aggregate condition but rather per space. Thus, a press box that is 2,500 square feet (232 m2) in area would need to be subdivided into areas less than 1,000 square feet (93 m2) each in order to be below the threshold for sprinklers. There is no specific requirement for the separation of these spaces. It is assumed, however, that the separation would be a solid barrier of some type but without a required fire-resistance rating. The provision is meant to mirror that in Section 1028.6.2.3, which exempts press boxes and storage facilities less than 1,000 square feet (93 m2) in area from sprinkler requirements in smoke-protected assembly seating areas."