eyan50495
REGISTERED
Hi All
I am trying to determine the fire alarm requirement for a composite wood joist (TJI / Glulam) ceiling. Ceiling height is 12' floor to floor with 24" TJIs.
Although I have an answer from the local fire alarm contractor and know that our county fire marshal points to NFPA 72, I still want to see where this requirement is in the code or if it is something the fire marshal is adding.
This is a commercial building 1 story + basement, mercantile use. Looking at NFPA 72 (2019), 17.7.3.2.4 lists the requirements for 'SOLID JOISTS'. Then it calculates the spacing of fire alarm detectors based on a percentage of depth of the structure to the ceiling height.
I don't see anything about composite joists/beams like TJIs and I am well aware they combust differently than solid or dimensional lumber. Is there a definition of solid joist or a requirement for composite joists I am missing? Similarly what would the requirement be if it was a steel joist? Is that considered 'solid'?
For reference, the FA contractor says that if the ceiling were to be left exposed, a fire alarm detector would be required between each joist (joists are 12" - 16" O.C.) which sounds ridiculous. The solution would be to put drywall over the entire ceiling so it could be considered a 'smooth ceiling'.
Thank you
I am trying to determine the fire alarm requirement for a composite wood joist (TJI / Glulam) ceiling. Ceiling height is 12' floor to floor with 24" TJIs.
Although I have an answer from the local fire alarm contractor and know that our county fire marshal points to NFPA 72, I still want to see where this requirement is in the code or if it is something the fire marshal is adding.
This is a commercial building 1 story + basement, mercantile use. Looking at NFPA 72 (2019), 17.7.3.2.4 lists the requirements for 'SOLID JOISTS'. Then it calculates the spacing of fire alarm detectors based on a percentage of depth of the structure to the ceiling height.
I don't see anything about composite joists/beams like TJIs and I am well aware they combust differently than solid or dimensional lumber. Is there a definition of solid joist or a requirement for composite joists I am missing? Similarly what would the requirement be if it was a steel joist? Is that considered 'solid'?
For reference, the FA contractor says that if the ceiling were to be left exposed, a fire alarm detector would be required between each joist (joists are 12" - 16" O.C.) which sounds ridiculous. The solution would be to put drywall over the entire ceiling so it could be considered a 'smooth ceiling'.
Thank you