CalSchoolArchitect
REGISTERED
- FIRE AREA. The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above."
We are adding 1 additional 960 sf portable classroom building (total building area - 6,720sf)(total occ's 366)
Total combined building area < table 506.2 basic allowable area for typeVB-E occupancy (6720sf<9,500sf)
The school site is a pre-SB575 non-fully sprinklered school site.
DSA (the Division of the State Architect/California) states that with the new building addition, the fire area will consist of more that 300 occ's and that all the portable classroom buildings grouped together as a single building will be required to be sprinklered per 903.2.3.3. ... or the new building will need to be relocated 20' away from the original (6) buildings and treated as a separate building.
Are they correct?
The definition of fire area includes floor area "enclosed ... by exterior walls..." Would not each separate portable classroom building be classified as it's own separate fire area.
your help is appreciated.