Sorry if I'm revisiting a topic, I'm new to this site and was unsuccessful in my topic search. My fault not the site.
The Maximum Allowable Quantity(MAQ) per control area tables in the fire code, were still using the 2006 version until March or April, uses the terminology use-open and use-closed. The code definitions for both are relatively straight forward, however depending on how the reader interprets both the table and the footnotes, the results can be drastically different. I'll will point out an example from Table 2703.1.1(1) from the 2006 FC version, and while other versions have changed the location of the table they read nearly the same.
Without using the allowable increases in the footnotes;
Class IA flammable Liquid. Allows 30 gallons in storage, 30 gallons in use-closed, and 10 gallons in use-open. Footnote "b" states the aggregate quantity - storage, use-closed, and use-open, cannot exceed the quantity listed for storage. In other words all together you are allowed 30 gallons.
Example:
Scenario #1. The container in storage is 30 gallons. I transfer 10 gallons into an open container and put the original 30 gallon container back in storage. The simple math tells me that I have 20 gallons in storage and and 10 gallons in use-open which would comply with footnote "b". However, most fire code officials will tell you that a 30 gallon container is always a 30 gallon container regardless of the remaining quantity, therefore there is 30 gallons in storage and 10 gallons in use-open - a violation of footnote "b".
Scenario #2. The same condition as above. I attended two separate seminars on this next subject and received two separate answers to my question as follows; is the 30 gallon container now considered use-closed or use-open? The first seminar answer was the 30 gallon container is now use-closed because the cap has been put back on. The second seminar answer was the 30 gallon container is now use-open because the original sealed cap has been removed.
I would like some input from this group on both scenarios because these greatly affect the MAQ's for buildings other than H occupancies.
The Maximum Allowable Quantity(MAQ) per control area tables in the fire code, were still using the 2006 version until March or April, uses the terminology use-open and use-closed. The code definitions for both are relatively straight forward, however depending on how the reader interprets both the table and the footnotes, the results can be drastically different. I'll will point out an example from Table 2703.1.1(1) from the 2006 FC version, and while other versions have changed the location of the table they read nearly the same.
Without using the allowable increases in the footnotes;
Class IA flammable Liquid. Allows 30 gallons in storage, 30 gallons in use-closed, and 10 gallons in use-open. Footnote "b" states the aggregate quantity - storage, use-closed, and use-open, cannot exceed the quantity listed for storage. In other words all together you are allowed 30 gallons.
Example:
Scenario #1. The container in storage is 30 gallons. I transfer 10 gallons into an open container and put the original 30 gallon container back in storage. The simple math tells me that I have 20 gallons in storage and and 10 gallons in use-open which would comply with footnote "b". However, most fire code officials will tell you that a 30 gallon container is always a 30 gallon container regardless of the remaining quantity, therefore there is 30 gallons in storage and 10 gallons in use-open - a violation of footnote "b".
Scenario #2. The same condition as above. I attended two separate seminars on this next subject and received two separate answers to my question as follows; is the 30 gallon container now considered use-closed or use-open? The first seminar answer was the 30 gallon container is now use-closed because the cap has been put back on. The second seminar answer was the 30 gallon container is now use-open because the original sealed cap has been removed.
I would like some input from this group on both scenarios because these greatly affect the MAQ's for buildings other than H occupancies.