This section has always confused me a bit, and every time I think I get it too much time passes and I lose it again.
I have a fire barrier, required by 416.2 for a paint room. In this fire barrier I have a 45-min door, with a wired glass vision panel exceeding 100inch². I am struggling with the path to the correct label for this glazing. Starting at 716.1.2.1, I understand the requirement for safety glazing, even with the wired glass. 716.1.2.2 then directs marking in accordance with all of the tables (1), (2) & (3). As subsections to 716.1.2.2 there are two sections that define the specific markings for either fire-protection-rated glazing, or fire-resistance-rated glazing. This is where I get sideways. I am not sure which I need.
If I look at 716.2.2.3.1 it appears that because of the size of the vision panel, fire-resistance-rated glazing is required. So do I look to t716.1(2) to determine the required markings? If I do that, I see the section for "other" fire barriers (which applies) which specifies "D-H", but there is no time (xxx) listed. This confuses me even more. And, using t716.1(2) I see the specific markings based on the size of the vision panel for fire barriers for exit elements. I assume those markings would not apply since I do not have a fire barrier being used in that manner.
Is the glass just marked "D-H", or should it be "D-H 45"? Or something completely different?
I have a fire barrier, required by 416.2 for a paint room. In this fire barrier I have a 45-min door, with a wired glass vision panel exceeding 100inch². I am struggling with the path to the correct label for this glazing. Starting at 716.1.2.1, I understand the requirement for safety glazing, even with the wired glass. 716.1.2.2 then directs marking in accordance with all of the tables (1), (2) & (3). As subsections to 716.1.2.2 there are two sections that define the specific markings for either fire-protection-rated glazing, or fire-resistance-rated glazing. This is where I get sideways. I am not sure which I need.
If I look at 716.2.2.3.1 it appears that because of the size of the vision panel, fire-resistance-rated glazing is required. So do I look to t716.1(2) to determine the required markings? If I do that, I see the section for "other" fire barriers (which applies) which specifies "D-H", but there is no time (xxx) listed. This confuses me even more. And, using t716.1(2) I see the specific markings based on the size of the vision panel for fire barriers for exit elements. I assume those markings would not apply since I do not have a fire barrier being used in that manner.
Is the glass just marked "D-H", or should it be "D-H 45"? Or something completely different?