CBC 2010 Are the doors in an apartment building required to have self closers on them, simular as say between an attached garage and dewelling?
 
Coug Dad said:
Which doors are you asking about? Corridor?
If a rated Corridor, 715.4.8.2 Automatic-closing fire door assemblies.

Automatic-closing fire door assemblies shall be self-closing in accordance with NFPA 80.
 
I agree with Mark too. If it's a fire-rated door (and it should be), it has to be self-closing and self-latching. It may also require gasketing depending on which code the doors were installed in accordance with.
 
CBC 1133B.2.5 Door opening force. Required fire doors shall have the minimum opening force allowable by the appropriate administrative authority, not to exceed 15 lbf
 