In the past I've used the entire building footprint longest diagonal to establishe the distance to divide by 2 or 3 to determine what distance between exits is required. I've almost exclusively used the IBC.... But I've always kind of questioned this mindset in some situations more than others.
Recently I got handed a project that the AHJ requires using NFPA101 and I've gotten reasonalbly familiar with it. There is some verbiage in there that has me thinking.....
Section 7.5.1.3.2 says-
To be considered remote, the exits, exit accesses and exit discharges in new buildings must be located at a distance "from one another not less than one-half (one-third if the building is fully sprinklered) the length of the maximum overall diagonal dimension of the building or AREA to be served".
This particular project is a relatively simple one. A covered pavilion that has restrooms. It's all open at the pavilion side with 2 gang toilets and a family restroom behind a privacy screen.
After reading the "area to be served" part I drew the diagonal just from corner to corner of the pavilion part.
Thoughts?
Recently I got handed a project that the AHJ requires using NFPA101 and I've gotten reasonalbly familiar with it. There is some verbiage in there that has me thinking.....
Section 7.5.1.3.2 says-
To be considered remote, the exits, exit accesses and exit discharges in new buildings must be located at a distance "from one another not less than one-half (one-third if the building is fully sprinklered) the length of the maximum overall diagonal dimension of the building or AREA to be served".
This particular project is a relatively simple one. A covered pavilion that has restrooms. It's all open at the pavilion side with 2 gang toilets and a family restroom behind a privacy screen.
After reading the "area to be served" part I drew the diagonal just from corner to corner of the pavilion part.
Thoughts?