I've heard from some inspectors that say it is not part of the scope of work on the permit so they can't enforce it. I see it differently.Fix it.
I agree. If the construction type is IB, then any penetration through the floor/ceiling assembly must have a 2-hour rating and should have been caught by the inspectors.I've heard from some inspectors that say it is not part of the scope of work on the permit so they can't enforce it. I see it differently.
Sorry, I was looking at the 2018 IBC, which has horizontal assemblies in Section 714.5. In the 2015 IBC and earlier, it was in Section 714.4. The paragraphs shifted when they inserted a new paragraph after Section 714.1.Que?
714.4 Horizontal assemblies. Penetrations of a fire-resistance-
rated floor, floor/ceiling assembly or the ceiling membrane
of a roof/ceiling assembly not required to be enclosed
in a shaft by Section 712.1 shall be protected in accordance
with Sections 714.4.1 through 714.4.4.
714.4.1 Through penetrations. Through penetrations of
horizontal assemblies shall comply with Section 714.4.1.1
or 714.4.1.2.
Exceptions:
The end result of both is fill it with grout and play through....