Looking to get some thoughts and or feedback on a fire pole for a small 2 story fire house.
Building will be non-separated but of course there will be some ratings such as the R use dorm area.
Second floor houses dorms and day room. Will want to meet the rating requirement for that use.
This fire chief wants a fire pole without any doors into the pole room / area. open at the top and open at the bottom for ease of use. I don't think that can happen.
712.1.9 item 4 states that the two story opening can not be open to a corridor of an R occupancy. which is basically what we would have. does providing a fire shutter at the opening into the R corridor make this issue go away if its tied into the fire alarm. this item 4 seems very definitive. It does not say "unless otherwise protected as required". Any thoughts?
Building will be non-separated but of course there will be some ratings such as the R use dorm area.
Second floor houses dorms and day room. Will want to meet the rating requirement for that use.
This fire chief wants a fire pole without any doors into the pole room / area. open at the top and open at the bottom for ease of use. I don't think that can happen.
712.1.9 item 4 states that the two story opening can not be open to a corridor of an R occupancy. which is basically what we would have. does providing a fire shutter at the opening into the R corridor make this issue go away if its tied into the fire alarm. this item 4 seems very definitive. It does not say "unless otherwise protected as required". Any thoughts?