• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fire pump room requirements

Hyrax4978

Registered User
Joined
Nov 28, 2016
Messages
205
Location
Hartford, CT
It was just determined a building we are designing will need a fire pump. where in the code do we find requirements for the room? Basically looking for ratings and the such.

Thanks,
Brian
 
How about for the diesel fuel tank that is between 150 and 200 gallons of fuel oil? rating the room is easy, but does that large quantity of fuel trigger anything else?
 
High rise or other
How about for the diesel fuel tank that is between 150 and 200 gallons of fuel oil? rating the room is easy, but does that large quantity of fuel trigger anything else?


Might be allowed a Day tank in the building and another tank somewhere else..

What kind of occupancy// business???
 
Is the fuel in the building? You would have to look at control area requirements....
Diesel fuel is a Class II combustible liquid, which is permitted 120 gallons. But since a sprinkler system is installed, the quantity can be increased by 100% to 240 gallons.
 
Chapter 4 in NFPA 20, Standard for the Installation of Stationary Pumps for Fire Protection, also has separation requirements for the Fire Pump room (basically, for high-rise it's 2-hr, for non-high-rise it's 1-hr).
 
# ~ #

What about the type of diesel fuel tank(s),
...single wall, double wall, containment
plans ?


# ~ #
 