Keystone
SAWHORSE
Townshouse developement, side by side units.
Lumber supplier shipped out unrated ply for the 4ft fire separation and OSB for interior roof in fill.
It involves a National Production Bldr. so they have 3 six pack units built and shingled.
Bldr wants to apply No-Burn or similar product to underside of roof sheathing as a remedy.
My opinion is a hard NO, the rating from sheathing is from both sides, top and underside.
Fire rated spray from the underside only protects just that, the underside.
We would still have a minimal unprotected narrow section of sheathing between party walls and no protection form the top side.
I believe the bldr is now speaking with its numerous Licensed D.P.’s...
Thoughts, Opinions?